Snow Sensor Yellow/ Blue / Brown  Wire Open / Short
Here are the testing instructions
 
 - Pull black from terminal
     7 so we are isolating the sensor
- Hold one lead of the ohm
     meter on the black wire
- Put the other lead on
     the blue (8).  This should be 2Mohms when sensor is dry and
     10-300Kohms when wet
- Put the other lead on
     red (6).  This should be 50 ohms
- Put the other lead on
     Brn/Slab (10).  Check the resistance chart in the manual.  This
     should correspond to slab temp
- Put the other lead on
     Yel (9).  Check the resistance chart in the manual.  This should
     be close to slab temp
 
If any of these are out of spec than you may have a bad slab
sensor
 
The error can only happen in one of 3 places.
 
 - Sensor itself
- Wiring like a bad
     splice, staple in wire etc
- Control itself
 
The only way to know is to isolate sensor and start
measuring.